> For what it's worth, most everyone at the marina where I kept my boat
> which was in a county park had GFCI problems when they first arrive, as
did most every guest from other yacht clubs. The county specified that
all the electric has to be GFCI protected. The actual fix to the problem
was universal.
> The problem is that all the boats with problems had inverters. he
inverters can be configured at least two ways. One is for neutral and
ground to be tied together, the other for them to be separated. The
inverters come from the factory with ground and neutral tied together,
this automatically trips the shore power GFCI. I have an Interphase
inverter. It has a screw that can go into one of two holes. In one hole
the ground and neutral are tied together, in the other hole they are
not. By going to the hole where they are not tied together, the problem
with tripping the GFCI was eliminated. Every boat that had the tripping
problem and had electricians come to fix the problem ended up with a
> similar solution.
> Jake
REPLY
That is the difference with "marine" and RV designated inverters.
Unfortunately if you simply disconnect the green connection d oyou make
sure the green safety wire is properly connected to the vessel
grounding/bonding system? Improperly done you simply create a shock
hazard.
Arild