Normally, the selector switch is only selecting the power for the DC
breaker panel. That is to say, it is not handling the several hundred
amps that the diesel starter motor needs. So, in my boat you can
disconnect everything except the starter motors with the selector switch
in off. Ideally, the starter motors should have their own high-current
cutoff switches mounted outside the engine room, but many (perhaps most)
don't. My 50' Marine Trader has these switches mounted inside the
engine room, and the switches have a warning to the effect that if they
ever have to cut off a shorted starter, they should then be replaced.
The PO wired around these switches, for reasons I am not sure of, but I
went back to them and they work fine. Probably he had some bad cable
end terminations with high resistance and blamed the switches. It is
very hard to find these really high amperage switches, as most of the
ones you find only handle up to about 200 amps and even my Perkins
T6-354 can exceed this on a cold day.