after the lightning strike we replaced our old heart 2500 inverter
charger with a new victron multi plus 2500.? We are now at anchor and
the charging function is not working properly.? It only puts in 20 amps
on bulk and then at about 13.5 volts shifts to absorption where it only
puts out 15 amps.? How do I set this?? I have six rolls wet cell
batteries about 960 amp hr total.
Check it on shore power, if it works then you have a generator problem.
Also, if using the battery temp sensor, un hook it and see how it works.
Also unplug the remote panel and check the units output. Make sure the
rheostat on the remote is turned all the way up. Also, use test
equipment separate from the battery monitor to measure the output as the
problem might be in the monitor.